Staff Answer
Jun 03, 2014 - 06:37 AM
Here is a answer from one of our experts.
"
Easiest would be to make an internal node NC
Have the breaker between NC and one node and the RLC branch between NC and the other node.
Another method would be to have variable RLC branch. Switch the Resistance of the RLC branch depending on the switch state.
"
--
George Wai,
Software Support & Development Specialist
Manitoba HVDC Research Centre
a division of Manitoba Hydro International Ltd.
211 Commerce Drive | Winnipeg, Manitoba, Canada R3P 1A3
T +1 204 989 1241 | F+ 1 204 989 1277
support@pscad.com | www.hvdc.ca | www.pscad.com
--