AC8B AVR Parameter (field limiter loop reference (VLV))
Dear Sir/Madam
I am writing this message in respect of the parameter in AC8B exciter model.
I am currently modelling a Synchronous condenser in PSCAD. According to the datasheet provided by the suppliers, I need to use the AC8B exciter model. However, I noticed that a parameter in AC8B AVR named field limiter loop reference (VLV) is not fully aligned with AC8B model addressed in "IEEE Recommended Practice for Excitation System Models for Power System Stability Studies"
In addition, I played around with this parameter and it was noted that it plays an important role in field voltage.
Therefore, could you please provide me with some explanation on field limiter loop reference (What's this for? What are the purpose to include such parameter?)
Thank you and I am looking forward to hearing from you
Best regards
Allen
Status:
Open Mar 25, 2020 - 06:31 AM
AC8B AVR
1answer
Answer
Mar 27, 2020 - 06:15 PM
VLV is the field voltage used in the minimum field voltage limiter loop.
Normally VEmin is zero. If FEX is positive then VEmin is VLV/FEX.
Answer this question
Share Your Own Experience & Expertise
We look to ensure that every question is answered by the best people with relevant expertise and experience, the best answers include multiple perspectives. Do you have relevant expertise or experience to contribute your answer to any of these commonly asked questions?
By
How is your AC8B now? For some reason, when I change voltage reference of AC8B, the terminal voltage of the gen is not changed at all.