So lately I've been trying to get a grapple on PSCAD to begin some research and I was given a simple 6 bus system with some solutions on the fault analysis for a 3 phase and single phase-ground fault. I worked through and developed a matlab code that MATCHES the solution given (1412<-81.5 Amps).
But when I develop the system in PSCAD and simulate the fault I cannot get the fault to match up.
I keep getting around 2160<-69.4 Amps.
I've gotten the powerflow to match up within a few percent of the actual power flow. I've triple checked or more all of my impedances.
Here are some pictures of the system.
I've been scratching my head for weeks now. I've triple checked everything and I can't for the life of me figure out why it's not matching up. My line impedances are correct. My generator and Transformer impedances are correct. My load flow is matching up. I've been throwing solutions at a wall to see if anything sticks but I can't get anything to give me the solution I want. So I've come here to hopefully get some help. I've attached my PSCAD file as well as the load flow and fault analysis solutions.
Part 1 results are the load flow solutions. Part 2 results are the fault analysis solutions.
If you have any further questions or suggestions please feel free to ask/comment.
PSCAD, 6 bus, Single Line to Ground
Do you have the same question? Follow this Question
This question has not yet been answered.
We look to ensure that every question is answered by the best people with relevant expertise and experience, the best answers include multiple perspectives. Do you have relevant expertise or experience to contribute your answer to any of these commonly asked questions?
By
Hi there,
I think your issue comes form load model. "For a static load model, the power relationship to voltage and
frequency is an exponential equation." see equation (1) and (2) in this reference "A Novel Approach to Solve Power Flow for Islanded Microgrids Using Modified Newton Raphson With Droop Control of DG"
Hope this will help you.
By
I have all of those parameters set to zero in the PSCAD model which essentially makes the equations:
PLk=PLk0
QLk=QLk0
So the load should equal what I have placed.
By
Dear there,
Try to modify it. Because you don’t know how matlab was model it’s load.
Also, you should know that at bus #1 the angle should be zero, so you should eliminate the value of the bus#1 from others bus in order to get zero degree at slack bus.